So then what is the max KW range on 6-3 NM Aluminum in a residence.
I get 16kW.
((240V?40A?1000)-8kW)/(5%?8kW)+12kW
Even for aluminum?
So then what is the max KW range on 6-3 NM Aluminum in a residence.
I get 16kW.
((240V?40A?1000)-8kW)/(5%?8kW)+12kW
I believe so. It's the 40A in the calculation.Even for aluminum?
A 16kW range would be calculated to present a maximum demand load per Note 1, i.e. 8kW is increased by 5% of 8kW per kW over 12kWA 16 kw range would be calculated to be 12kw or am I talking out my -- you know what-- again. 12000/240= 50 amps.
Now this is resi work so I will guess the man is using copper as I have not seen 6/3 aluminum but if it were aluminum then it would be ser cable , I presume and that would only be rated 40 amps.
A 16kW range would be calculated to present a maximum demand load per Note 1, i.e. 8kW is increased by 5% of 8kW per kW over 12kW
16kW - 12kW = 4kW
5% of 8kW = 400W
4?400W?1000 = 1.6kW
8kw+1.6kW = 9.6kW
9.6kW?240V = 40A
A 16kW range would be calculated to present a maximum demand load per Note 1, i.e. 8kW is increased by 5% of 8kW per kW over 12kW
16kW - 12kW = 4kW
5% of 8kW = 400W
4?400W?1000 = 1.6kW
8kw+1.6kW = 9.6kW
9.6kW?240V = 40A
As long as you don't blame yourself, I'll let you slide...... I am having a bad week-- I'll blame the drugs. :grin: