Even for aluminum?
I believe so. It's the 40A in the calculation.

For copper it'd be:

((240V?55A?1000)-8kW)/(5%?8kW)+12kW = 25kW

I'm open to correction. These are my first instances of reverse calculating from wire size and type to kW rating.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A 16 kw range would be calculated to be 12kw or am I talking out my -- you know what-- again. 12000/240= 50 amps.

Now this is resi work so I will guess the man is using copper as I have not seen 6/3 aluminum but if it were aluminum then it would be ser cable , I presume and that would only be rated 40 amps.
 

Smart $

Esteemed Member
Location
Ohio
A 16 kw range would be calculated to be 12kw or am I talking out my -- you know what-- again. 12000/240= 50 amps.

Now this is resi work so I will guess the man is using copper as I have not seen 6/3 aluminum but if it were aluminum then it would be ser cable , I presume and that would only be rated 40 amps.
A 16kW range would be calculated to present a maximum demand load per Note 1, i.e. 8kW is increased by 5% of 8kW per kW over 12kW

16kW - 12kW = 4kW
5% of 8kW = 400W
4?400W?1000 = 1.6kW
8kw+1.6kW = 9.6kW
9.6kW?240V = 40A
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A 16kW range would be calculated to present a maximum demand load per Note 1, i.e. 8kW is increased by 5% of 8kW per kW over 12kW

16kW - 12kW = 4kW
5% of 8kW = 400W
4?400W?1000 = 1.6kW
8kw+1.6kW = 9.6kW
9.6kW?240V = 40A

You nailed it. Both times. :cool:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
A 16kW range would be calculated to present a maximum demand load per Note 1, i.e. 8kW is increased by 5% of 8kW per kW over 12kW

16kW - 12kW = 4kW
5% of 8kW = 400W
4?400W?1000 = 1.6kW
8kw+1.6kW = 9.6kW
9.6kW?240V = 40A

well that's fine but if you think like I do ( I am glad you don't) you screw everything up. :) For some reason I used 16 kw- 8 kw and got 8 kw instead of 16- 12 and getting 4kw.

From there I screwed up even further by using 50% instead of 5%. .5 vs .05

As usual you are correct. I am having a bad week-- I'll blame the drugs. :grin:
 