Greg a SABC must cover countertop recep. The microwave above the range is not a countertop area. 210.52(B) (C)
Well Jim we all know how opinionated you are and you probably just hurt Cavie's feelings-- he is an inspector
Yes, I understand the microwave/vent cannot be served by the sabc but I have been told many times that the microwave/vent must be installed on a separate dedicated circuit. I have been told this by inspectors. The only reference I see is 422.16b4. This is for range hoods. However, one might interpret a range hood as something different than a microwave/vent unit.
Good point. Also if we start allowing fixed loads on a SA circuit just where do we stop. Add DW, GD. NEC says what it says. NEC never says if it is too costly or hard to do that we can ignore it.Every single over the range micro I have seen is also a range hood. 110.3b is also in play.
I took a look at Sears installer site to see if they give a price. Well in CA the charge about 189.00 depending on Zip to add an outlet and a little over 100.00 to hang the over the range Micro.
I wonder how they can make such a promise of price?
If my feeble minds is working I remember Bob looking into this an stating that a microwave range hood was listed as a microwave and not a hood. However, as I stated before this rule was written to deal with changes from hood to microwave. I have never seen a range hood come with a cord and plug.Every single over the range micro I have seen is also a range hood. 110.3b is also in play.
I doubt if that "add an outlet" means they will run a dedicated circuit. They get there and no circuit is available and then they tell you how much to run a dedicated circuit.
That $189 just covers the cost of adding a receptacle in the cabinet over the microwave.
If my feeble minds is working I remember Bob looking into this an stating that a microwave range hood was listed as a microwave and not a hood. However, as I stated before this rule was written to deal with changes from hood to microwave. I have never seen a range hood come with a cord and plug.
You might be right on the listing. However, it is certainly a range hood. I think that's pretty obvious.
I totally agree-- It was Bob who started that whole thing. :grin:
You might be right on the listing. However, it is certainly a range hood. I think that's pretty obvious.
If UL calls it a microwave it is a microwave even if it looks like a blender.
As a smart guy said '110.3b is also in play.' :grin:
I tend to not be a huge fan of 110.3b or the UL. Just for the reason you just posted. I prefer common sense over some geek in a lab.
So lets say we Deleat 110.3(B) .Who would test all the equipment that we install?
Rember most of this equipment is comeing in from china.:roll: