Cody K said:Could you show me where in the code this is referenced?
210.52(B)(2)
Cody K said:Could you show me where in the code this is referenced?
stickboy1375 said:210.52(B)(2)
Cody K said:I seen that, I guess I am stretching a bit when I would say a receptacle in a cabinet above microwave would be considered a wall receptacle or a countertop receptacle.210.52 B 1
Cody K said:I seen that, I guess I am stretching a bit when I would say a receptacle in a cabinet above microwave would be considered a wall receptacle or a countertop receptacle.210.52 B 1
infinity said:If the micro is fastened in place it would require it's own branch circuit since it would likely exceed the 50% rule, so it wouldn't matter if it were permitted on a SABC or not.
Cody K said:If you took that microwave and set it on the kitchen counter and plugged it in there everything would be fine. If a receptacle was installed for only the micro in a cabinet, what would be the difference, nothing.
Cody K said:I guess the point I was getting to is what Dennis mentioned earlier. If you took that microwave and set it on the kitchen counter and plugged it in there everything would be fine. If a receptacle was installed for only the micro in a cabinet, what would be the difference, nothing.
hillbilly said:I still haven't decided what to do......
I've been busy with other things, and have been letting this problem "stew" in my brain.....kinda on the back burner.
This range and microwave are located on a outside basement (concrete block) wall.
I guess that I could mount a NEMA 4 panel on the outside wall, feed it with the 6/3 NMB and then power back thru the wall to the range and microwave.....although I may have a problem with 110.26(E) as there is a deck over this (sloped) area, and I may not have the headroom.
This seems really redundant just to meet a code [110.26(A)] that is not clear (IMO) to begin with.
I'm just venting, I understand the "intent" of the code rule, and know
what I have to do:roll: .
I've got the customer looking for a microwave that pulls less than 10 amps (120V) and that will fit the space.
If he finds one, I can put it on the 20A (dedicated) dishwasher circuit.
This is my best option.
Running a new Homerun is not a option, microwave or not.
Any thoughts?
thanks