So what do you do when the range has no bottom drawer?
422.31 Disconnection of Permanently
Connected Appliances
(B) Appliances Rated over 300 Volt-Amperes. For permanently
connected appliances rated over 300 volt-amperes,
the branch-circuit switch or circuit breaker shall be permitted
to serve as the disconnecting means where the switch or
circuit breaker is within sight from the appliance or is capable
of being locked in the open position. The provision for
locking or adding a lock to the disconnecting means shall be
installed on or at the switch or circuit breaker used as the
disconnecting means and shall remain in place with or without
the lock installed.
Section 422.31(B) requires a special locking device for service
and maintenance personnel. A device that is attached to
the circuit breaker handle by a set screw is not an acceptable
means to serve as a safe method of locking the device in the
“off” position. The device must have provisions for placement
of a lock on it to secure the device in the “off” position.
The lockout device must be part of the disconnect assembly
and must remain in place after the padlock is removed,
whether it is a fused disconnect switch, a single circuit
breaker, or a circuit breaker in a panelboard. See 422.33(B)
for electric ranges.
Edited because I posted by mistake while I was researching
-Hal