gndrod said:
The 220.55 uses the word 'calculate', the 2008 Article 422.10(A) has been revised to use the word 'size' in accordance with 210.19(A)(3). What is your interpretation on why the CMP made that change? Just curious. rbj
I don't see that the word change did anything except make you go through several code sections to come back with the same answer we had to start with.
210.11 instructs you to supply branch circuits for appliances with an ampacity as calculated in 220.10.
220.10 specifies that you use table 220.55 to calculate a range load.
422.10 also specifies that 220.55 is used to calculate the load but also tells you to "size" it according to 210-19(A)(3).
210.19(A)(3) specifies that the branch circuit must be adequate for "the load to be served" but does not make any other statement about how that load is determined. It does go on to say that the circuit must be rated 40-amps for any range rated 8 3/4 KW (8750 watts) OR MORE. So without any instruction to the contrary, it seems that 220.55 is again used to "size" the branch circuit.
All that brings us back to sizing the branch circuit to serve the load as calculated using 220.55. We are not presented with an alternative. If the intent was that the branch circuit must be sized to provide the full nameplate, it would say so. It seems clear to me that the 220.55 value is what we are to use.
220.55 clearly shows that the "load" for a single 12KW range is calculated to be 8KW. 8KW at 240 volts is about 34 amps, but since 220.19 tells us that a 40 amp circuit is required for a range rated at 8-3/4 KW OR MORE, we must install a minimum 40-amp circuit. Then 210.24 allows us to install a 50-amp receptacle on a 40-amp circuit.
At this point everyone should be happy and all of the applicable sections of the code should be satisfied.
Whew! I don't know about you, but I am exhausted. NOTHING should be this complicated.