Greeting all I am looking for feedback on the following quiz question
A residential customer with a 120/240 Volt single phase service is converting from gas to electric cooking and has purchased a range for you to install with a 50 Amp cord and a nameplate of 16.2 kW.
210.19 States branch circuits shall have an ampacity no less than the maximum load to be served. What is the calculated load and non NMB cable size for the new branch circuit?
A) 9600 VA, #8 NMB
B) 12000 VA, #6 NMB
C) 16200 VA, #4 NMB
D) 17010 VA, #4 NMB
A residential customer with a 120/240 Volt single phase service is converting from gas to electric cooking and has purchased a range for you to install with a 50 Amp cord and a nameplate of 16.2 kW.
210.19 States branch circuits shall have an ampacity no less than the maximum load to be served. What is the calculated load and non NMB cable size for the new branch circuit?
A) 9600 VA, #8 NMB
B) 12000 VA, #6 NMB
C) 16200 VA, #4 NMB
D) 17010 VA, #4 NMB
A