In existing installations you can install a new range or dryer if you meet all the exceptions,
Here is some commentary from 2005 Handbook. 250.140
Caution should be exercised to ensure that new appliances connected to an existing branch circuit are properly grounded. An older appliance connected to a new branch circuit must have its 3-wire cord and plug replaced with a 4-conductor cord, with one of those conductors being an equipment grounding conductor. The bonding jumper between the neutral and the frame of the appliance must be removed. Where a new range or clothes dryer is connected to an existing branch circuit without an equipment grounding conductor, in which the neutral conductor is used for grounding the appliance frame, it must be ensured that a bonding jumper is in place between the neutral terminal of the appliance and the frame of the appliance.
The grounded circuit conductor of an existing branch circuit is still permitted to be used to ground the frame of an electric range, wall-mounted oven, or counter-mounted cooking unit, provided all four conditions of 250.140, Exception, are met. In addition, a revision in this provision for the 2005 Code permits application of the exception only where the existing branch-circuit wiring method does not provide an equipment grounding conductor. There are many existing branch circuits in which nonmetallic sheath cable with three insulated circuit conductors and a bare equipment grounding conductor was used to supply a range or clothes dryer. The bare equipment grounding conductor was simply not used because it was permitted to ground the equipment with the insulated neutral conductor of the NM cable. This ``extra'' conductor was on account of the fact that the bare conductor in a Type NM cable is to be used only as an equipment grounding conductor and cannot be used as a grounded (neutral) conductor in the same manner as is permitted for an uninsulated conductor in the service entrance.
In addition to grounding the frame of the range or clothes dryer, the grounded circuit conductor of these existing branch circuits is also permitted to be used to ground any junction boxes in the circuit supplying the appliance, and a 3-wire pigtail and range receptacle are permitted to be used