210.23 Permissible Loads.
In no case shall the load exceed the branch-circuit ampere rating. An individual branch circuit shall be permitted to supply any load for which it is rated. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
I'll give it a shot.jwelectric said:As I have asked more than one time could someone explain away these words that are found in 210.19(A)(3)
For ranges of 8? kW or more rating, the minimum branch-circuit rating shall be 40 amperes.
Yes there are, and no he didn't. IMHO Mike has misinterpreted the wording, but you and Bob are misinterpreting Mike's misinterpretation. IMO, Mike is not changing "minimum" to "maximum." Rather, Mike is incorrectly interpreting the word "minimum" to mean "sufficient," in too broad a manner.georgestolz said:Mike, you are adding something to that last sentence. You are changing the word "minimum" to maximum. There's no two ways about it.jwelectric said:The way I read it is that I could install a 27kw range on a 40 amp circuit
charlie b said:I agree with Bob and George on that. The rating of branch circuit conductors shall be not less than the maximum load to be served. [/list]
WARNING: The following is fiction. It is my wish list. It may or may not bear any resemblance to the NEC.
charlie b said:Therefore, if the range is 12KW, I would include a load of 8KW for the purposes of the service load calculation. But I would use 12KW (i.e., 50 amps at 240 volts) for the purposes of sizing the branch circuit. [/list]
I am more than willing to withdraw from this position, if anyone can prove that the code says otherwise. I am willing to concede, for example, that though a range is rated for 12KW, it is unlikely that the cook will be simultaneously running all four burners and the oven at max capacity.
m73214 said:So on a 12KW range, is the maximum load 12KW or is it 8KW from 220.55 Column C? The way I read this, I could have a 12KW range on a circuit rated at 8KW. Or am I wrongly thinking that Demand and Load are the same thing?
m73214 said:I agree completely. The way the codes reads now, I could have a 12KW range on a circuit designed for 8KW with #8 CU on a 35A breaker per 220.55 Note 4.
This last sentence clearly states that the MINIMUM circuit allowed for a range 8 ? kw or more RATING is 40 amps
but do you think I should install for maximum size? (remeber 8/3 romex is over a dollar a foot and rising}
jeff43222 said:So the 14.4 kW range I mentioned when I started this little discussion should be on a 60A circuit? 14.4 kW ? 240V = 60A.
Take two aspirin, a shot of Tequila, and call us in the morning.suemarkp said:This is one of those times that I agree with Mike.
What do you think after my last post? Does that effect your thinking? A 14.4kW range should get a 40A circuit, under the concensus.However, every house I've seen built in the last 10 years has a 40A range circuit and an installed range that is 10KW or more. So either everyone is doing something wrong, or else the consensus here is wrong.
RUWired said:No, the minimum branch circuit rating for single ranges 8-3/4 or more is 40a.
georgestolz said:What do you think after my last post? Does that effect your thinking? A 14.4kW range should get a 40A circuit, under the concensus.