Yes, I believe the code permits the OCPD to be up to 150% of the nameplate, and I see that as a hard maximum, not permitting you to use the next larger standard size where the 150% value is not a standard size. Note that an overcurrent specification on the nameplate or in the instructions would prevail over the code rule of 150%.Yes the unit states 40 amp but does not state that is the maximum... That is my point. If the unit is 16 kw and was on a commercial setting then we could put this on a 70 amp overcurrent protective device.
So you are saying I can go 150% of the units nameplate
I have never seen a range that can be fed with 2 circuits... perhaps commercially
As far as the two circuit rule, it only applies to "household type appliances", whatever those are, but no matter what they are, I think that rules out applying 422.11(B) to commercial ranges.