jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
1. OK it seems SMA RSS complies with NEC 2014, and only maybe with NEC 2017.
Anyone disagree that the SMA RSS complies with NEC 2014?
2. There is the Device (at array) and the Controller (near MSP or Inverter).
Some control circuit must be run to connect the two.
Is it Code Compliant to run the control wiring (low voltage wire) from the Device at array to the Controller along with DC circuit conductors in EMT down off roof?
I figure that would save major time of running separate conduit and/or ugliness of stapling cable to wall.
3. I seem so intrigued by this Rapid Shutdown discussion all of a sudden .....not sure why....maybe b/c I just got my first building permit plan-set rejected for lack of RSS:weeping::weeping:. Ahhh 2017.
I am employing an SMA 5.0 Inverter, so I plan to use the above SMA solution. Reasons: same make, works with SPS. We are on NEC 2014.
Probably not compliant to run the control wire with the PV circuits. Maybe if the instructions say you can, and the whole system is listed to UL 1741, you could make an argument. Seems like a stretch.
Secondary question is whether the control wire needs to be in a raceway.