If I have a roof mounted solar system in a commercial building, and the designer is installing the inverters within 10ft of the array, do the inverters need to be listed as rapid shutdown device? The Designer is stating they do not need to be listed since they are located withing 10ft of the array. Are the "controlled conductors" the conductors only from the array to the inverter, or are they the conductors from the array all the way to the service panel?
PV system circuits installed onor in buildings shall include a rapid shutdown function that controls specificconductors in accordance with 690.12(1) through (5) as follows:
(1) Requirements for controlled conductors shall apply only to PV systemconductors of more than 1.5 m (5 ft) in length inside a building, or more than3 m (10 ft) from a PV array.
“(2) Controlled conductors shall be limited to not more than 30 volts and 240volt-amperes within 10 seconds of rapid shutdown initiation.
“(3) Voltage and power shall be measured between any two conductors and betweenany conductor and ground.
“(4) The rapid shutdown initiation methods shall be labeled in accordance with690.56(C).
“(5) Equipment that performs the rapid shutdown shall be listed andidentified.”
PV system circuits installed onor in buildings shall include a rapid shutdown function that controls specificconductors in accordance with 690.12(1) through (5) as follows:
(1) Requirements for controlled conductors shall apply only to PV systemconductors of more than 1.5 m (5 ft) in length inside a building, or more than3 m (10 ft) from a PV array.
“(2) Controlled conductors shall be limited to not more than 30 volts and 240volt-amperes within 10 seconds of rapid shutdown initiation.
“(3) Voltage and power shall be measured between any two conductors and betweenany conductor and ground.
“(4) The rapid shutdown initiation methods shall be labeled in accordance with690.56(C).
“(5) Equipment that performs the rapid shutdown shall be listed andidentified.”