Rapid Shutdown with SolarEdge Optimizers in 2:1 series module design

Status
Not open for further replies.
690.12(B)(2)(1). This allows systems that are UL listed for RSD to be installed. Per 690.12(B)(2), the system only needs to comply with one of the following. So (B)(2)(2) & (B)(2)(3) don't apply if it is UL listed for RSD. Also see page 13 of the Synergy inverter manual which discusses the UL3741 listing.
 
690.12(B)(2)(1). This allows systems that are UL listed for RSD to be installed. Per 690.12(B)(2), the system only needs to comply with one of the following. So (B)(2)(2) & (B)(2)(3) don't apply if it is UL listed for RSD. Also see page 13 of the Synergy inverter manual which discusses the UL3741 listing.
You are a little late to the party. :D
 