RE: 300.22c - Other Space Used for Environmental Air
Art 300.22 C states "applies to space used for environmental air-handling purposes other than ducts and plenums" ... "It does not include habitable rooms or handling." (FPN states "The space over a hung ceiling used for environmental air-handling purposes is an example of the type of other space to which this section applies."
We have an AHJ which has tagged us for having a utility closet, with a door, which contains only a residential gas furnace. The return air enters the compartment via a grill, and is allowed to circulate into the furnace's air handler.
His contention is that this space's primary purpose is for air handling. We disagree, based on the the use of the phrase "primary use". We see this to mean that the space's ONLY purpose is to move air, not incidental to this use. (It's not that big deal to use ACT cable, but we feel that he is wrong and would like to at least have the option to wire it with NM cable.)
We referenced page 274 of the 2005 NEC Handbook, but the AHJ believes that this publication further supports his position.
(The AHJ is part of a government agency).
Does anyone know of any reference where this this has been interpreted or further examined? It's been disputed for over a year and we would like to get this settled.
Art 300.22 C states "applies to space used for environmental air-handling purposes other than ducts and plenums" ... "It does not include habitable rooms or handling." (FPN states "The space over a hung ceiling used for environmental air-handling purposes is an example of the type of other space to which this section applies."
We have an AHJ which has tagged us for having a utility closet, with a door, which contains only a residential gas furnace. The return air enters the compartment via a grill, and is allowed to circulate into the furnace's air handler.
His contention is that this space's primary purpose is for air handling. We disagree, based on the the use of the phrase "primary use". We see this to mean that the space's ONLY purpose is to move air, not incidental to this use. (It's not that big deal to use ACT cable, but we feel that he is wrong and would like to at least have the option to wire it with NM cable.)
We referenced page 274 of the 2005 NEC Handbook, but the AHJ believes that this publication further supports his position.
(The AHJ is part of a government agency).
Does anyone know of any reference where this this has been interpreted or further examined? It's been disputed for over a year and we would like to get this settled.