Re circuit on resid. load

Status
Not open for further replies.

George Stavrou

New member
problems: IVisit a resintecial project The inspector pass and I question the # of points on # 14 romex, The inspector insist no maximun, he claim unlimited I claim max load on this circuit is for cont. load =80% and every point, recept. or lighit shall be count as 180 va. Do I interp. the code The whrong way? Please advise me Thank you
 
For residential installations the inspector is correct, the 180 VA applies only to other than residential installations.

Welcome to the forum.:)
 