Re-identified ungrounded conductors

Status
Not open for further replies.

session88

Member
Location
USA
An electrical contractor doing installations in the power plant I work in ran out of brown, orange and yellow #8 awg wire for some 25 HP motors they were wiring up. Found them using #8 awg GREEN wire because that is all they had at the time. They were using black shrink tube (with a heat gun) to reidentify the entire length of the three 480 volt phases to the motors. Is this a code violation according to arcticle 250.119?
 
Found them using #8 awg GREEN wire because that is all they had at the time. They were using black shrink tube (with a heat gun) to reidentify the entire length of the three 480 volt phases to the motors. Is this a code violation according to arcticle 250.119?
Not only is it a violation - it's a serious waste of time, and therefore money to do so (Especially since they might be doing the installation twice...) - where is the nearest supply house? If it is on the way in to the job, the next day - they could have gone home - picked some up the next morning and done the job right once....
 
Code violation for sure. you can NOT use green for anything other than ground. Even if it is re-identified.

~Matt

Well, maybe. Until the 2005 NEC this was not a violation. Green was required for the EGC but was not restricted to the EGC.
 