In Mass we don't have 250.130(C)
But, but, I thought the NEC came from Mass.:-? :roll:
No, seriously, what is the intent? They don't allow EGC's separate from the circuit conductors?
In Mass we don't have 250.130(C)
Mkgrady, The code says what it says. It says ( for what ever code cycle your using) that
if you are going to install something, these are the rules. For example: it doesn't say it's ok
to reuse nm with a full size egc, it says 15a, 20a, and 30a branch circuits shall have an
egc the same size as the circuit conductors. So. to install a code compliant 15,20, or 30a
device, that circuit must have an egc the same size as the circuit conductors, by extending
a circuit ( 15,20,30) with an egc smaller than the circuit conductors a code violation has
been made. I hope this helps what your looking for.
But the extension has a full size EGC, and the old romex does meet code. If it was against the code for the existing circuit to be there it would have to be removed. Boy would that keep us busy!.
I'm not saying anybody is wrong. I just don't think the code is clear one way or the other. Plus most things in the code make sense and this doesn't to me. ......
Maybe that's why I didn't get the job - but then again at least I won't get sued some day. (my fault or not)
You understand that a new outlet must be supplied with a full size EGC, right?
So if the EGC starts out under sized at the panel and the only place it is full size is at the wire you added how can you say the outlet is supplied with a full size EGC?.
I really just want to understand what the code requires when circuits are extended from these old cables.
I am also from MA I agree with M. D.s interpretation of MA rule 3 and the NEC.
If you install a new receptacle outlet it must have a full size EGC back to the source. There is no exception for this.
Will an electrical inspector let it slide, ya sure they might.
Mkgrady
In reading your posts, it sounds like you are allowing confusion to permit you to install a violation.
Whether you have confusion or not, it is a violation.
So, just put that thought into your head and realize it is not permitted and move on.
if the smaller ground wire is a concern then I would just use GFCI breakers on the circuits in question.Or the inspector could site rule #1 of the Mass code as the installation could be considered NOT reasonably safe to persons and property because the reduced equipment grounding conductor of the existing branch circuit would not provide a sufficient low-impedance path for ground fault current of the new installation that would be connected to it.
No it wouldn't ,.. let's say the original wire has not been stapled with insulated staples but has a full size GC ,.. the lack of proper stapling would not preclude from using the original wire .
So are you saying that the un-insulated romex staples that I've used all my life and that the supply houses sell isn't legal to use on romex? Who or where does it say that the staples have to be insulated? Silly I say!!
....Where staples are used for cable sizes smaller than 8 AWG conductors, they shall be of the insulated type, or listed noninsulated staples driven by staple guns shall be permitted....
I don't feel confused. I just don't see it the way you and others do. I haven't read any group of words from here or the code book that tell me I can't do what I'm asking about.
Herein lies your confusion.
Is this supposed to be helpful, funny or insulting?