arcsnsparks98
- Jackson, TN USA
Not long ago there was a thread about a chiller with a control cabinet labeled 5kA SCCR. I believe it was a 208 chiller. I recently saw an install of two 480v chillers, each having their own control cabinet with a 5kA SCCR. They were fed with a 600A MCCB, 65kAIC (each) and located approximately 100' from the switchgear. Parallel 350 Cu feeders so negligible current limitation there. The transformer supplying the gear is a 2000 kVA delta/wye to a 2500A OCP protecting the entire switchgear. Most transformers of this configuration that I come across (please contain the 'nit picks') are usually marked with a Z of about 5.5%, give or take a fraction of a % here and there. Clearly there is more than 5kA available at the chillers. The way I calculate it though, any transformer large enough to supply the chillers with sufficient operating current will be capable of delivering more than 5kA of short circuit current. Is this correct? Even with an isolation transformer, line reactor, etc. in place, it seems that there will be more SCC than what these cabinets are listed to handle. Thoughts?