RE: Volage Drop
Well the poco came out and changed transformer. But did not change out the 1/0. They told the homeowner that their calculations for it showed it was fine. Lights still dim when a load is started such as ac. I need some definite answers.
Under this scenario is the service ok? There is 1/0 triplex ran 200' overhead from the transformer to the meter. 4/0 URD ran 250' underground in conduit
to panel. The total house load is 110 amps. Before a load there is 246v at the meter and 241 at the panel. When a 110a load is online there is 231v at the meter and 230v at the house. Shouldn't the vd calculation for the 1/0 include the distance from the meter to the panel?
Does running overhead make any distance on length calculations? When I learned to calculate voltage drop nobody made any distinction between in conduit or overhead when it came to voltage drop because of length.
I'm going to talk to the poco again tomorrow to see if it was just a mixup with their linemen or what. I need all the ammunition I can find.