Readily accessible disconnecting means

Status
Not open for further replies.

lj

Member
Location
Tampa, FL, USA
My campus project has an existing six-breaker service panel in a fenced area in the middle of the property, 200' away from the buildings it serves. Each service disconnect feeds a main breaker panel outside each building. May we consider the main breakers outside each building as the "readily accessible disconnecting means," or, must we have documented switching procedures and installations monitored by qualified individuals per 225.32 Exception 1? Thank you. [Please note that this is a simplification of an earlier post.]
 
May we consider the main breakers outside each building as the "readily accessible disconnecting means,"

If I understand your situation correctly you would have a main breaker panel installed on the exterior of each building to supply the buildings correct?

If that is the case then the main breaker in these panels can count as the disconnecting means for the buildings as required in 225.32.

Chris
 
Readily accessible disconnecting means

I appreciate your quick reply, Chris. Yes, there is a main breaker panel on the exterior of each building to supply the building. Thanks.
 