snoogins1236
Member
- Location
- Colorado
- Occupation
- Electrician
Readings were at the junction box above the well pump, yes motor was running at time of readings.Where did you take these readings, and was the motor running at the time?
Readings were at the junction box above the well pump, yes motor was running at time of readings.Where did you take these readings, and was the motor running at the time?
Readings were at the junction box above the well pump, yes motor was running at time of readings.
I don't see the point in a summary but there is NOT a neutral, he only thought it did. Any 120V readings would be from the ground. Which brings another point from his pics in which apparently the EGC was optional that day.... As in not connected to the party in the disconnect.Since this thread meandered, it is probably worth a bit of a summary.
The only thing confusing about your report is that you have 120V and 310V, not 240V and 310V. To totally nail this down you would need to take all 6 measurements (Black-Yellow, Red-Black, Red-Yellow, Black-Gnd, Yellow-Gnd, Red-Gnd). However if the pump is working I'd say you don't need to fully nail this down, and just say 'The 310V is not unexpected and the pump is working, so all is fine.'
-Jonathan
I don't think those are pictures from his project. He couldn't post his.I don't see the point in a summary but there is NOT a neutral, he only thought it did. Any 120V readings would be from the ground. Which brings another point from his pics in which apparently the EGC was optional that day.... As in not connected to the party in the disconnect.
Taking measurements inside the control box is not very practical because as the OP found out, they are designed in a way that nothing is connected when the hood is off, and that is on purpose, because of that exploding capacitor.
Generally I will just take my pump readings at the well head which gives me enough data to know what's going on 95% of the time. Usually current brings more information than voltage.
The purpose of the summary was to be helpful to the OP and those that will come on this discussion at a later date. Something you have failed to do so far.I don't see the point in a summary but there is NOT a neutral, he only thought it did. Any 120V readings would be from the ground. Which brings another point from his pics in which apparently the EGC was optional that day.... As in not connected to the party in the disconnect.
Taking measurements inside the control box is not very practical because as the OP found out, they are designed in a way that nothing is connected when the hood is off, and that is on purpose, because of that exploding capacitor.
Generally I will just take my pump readings at the well head which gives me enough data to know what's going on 95% of the time. Usually current brings more information than voltage.
Don't agree. I think they are if you read back.I don't think those are pictures from his project. He couldn't post his.
Would it also then be helpful or antagonistic to bring up the concerning mention of "neutrals" and 120V, when there is nothing in any of the circuits to support that fact? Like any EC would both read what is on that disconnect, and simply open it know there is no neutral there. To be right honest, this is more like a homeowner type thread than an EC.The purpose of the summary was to be helpful to the OP and those that will come on this discussion at a later date. Something you have failed to do so far.
Yup, you're right. I thought he linked us to someone else's.Don't agree. I think they are if you read back.
If that is a consideration there is the Report button that can be clicked and it will send an alert to the forum moderators who will consider the content of the thread and decide if it should remain open. As of yet no reports have been sent, as such the thread is open for discussion so that the OP and anyone else can learn.Would it also then be helpful or antagonistic to bring up the concerning mention of "neutrals" and 120V, when there is nothing in any of the circuits to support that fact? Like any EC would both read what is on that disconnect, and simply open it know there is no neutral there. To be right honest, this is more like a homeowner type thread than an EC.