Senior Member
Then perhaps you had current and some kind of wild floating voltage at the meter that made a high V*I product.Yes it is a 2 wire meter with phase and neutral incoming and outgoing.
Then perhaps you had current and some kind of wild floating voltage at the meter that made a high V*I product.Yes it is a 2 wire meter with phase and neutral incoming and outgoing.
Correct- though if metering only two legs of 120/208Y, you would need a 12S (ie, 5th jaw). Assuming the OP's profile matches the location in question most likely its a single stator, single current coil meter (2 wire) which would require a neutral for the voltage coil:
![]()
Very true, I agree.
But here is one theory I have: If the neutral and line are somehow swapped at the meter, grounding the neutral after the meter can cause current flow from the utility neutral through the meter's current coil and down through the ground going back to the LV supply transformer. This current could be substantial given the right network conditions, ie if all the customers are TT and the voltage drop across the utility neutral is great enough.
Nice Theory, however if that were the case, somewhere along the line of 500 to 1500 amps would have had the flow on that neutral for the 12 to 24 hour., depending on sahibs average electrical use, to make that meter read three times normal for the month. Pretty sure that amount of current would fry anything in a residence.
I don't know about India, and it's been too long since we had a mechanical meter here, however I seem to recall that if the Poco estimated your power use for that month, that it was on the bill somewhere for that month. I still think that low previous month's estimations combined with an actual meter reading when the neutral was fixed is what resulted in the higher bill.
Then perhaps you had current and some kind of wild floating voltage at the meter that made a high V*I product.
Did not really give it a lot of thought other than thinking if the current was close to normal then that only left the voltage to be crazy abnormal to result in such a crazy amount of power recorded.Wouldn't the floating voltage be lower than 230 volts? I am not saying you are wrong as this is your area of expertise- just curious how the physics of an EM meter work to produce such a high reading with low fluctuating voltage on my part.
Did not really give it a lot of thought other than thinking if the current was close to normal then that only left the voltage to be crazy abnormal to result in such a crazy amount of power recorded.
I just made a wild swing that if the meter had no voltage reference then it might have floated to most anything. Sorry but I did not give it much expert thought but just a passing thought based on tying down one of the two variables in the power equation.
That is my thought as well.I myself have trouble believing that the meter actually recorded 3x the amount of energy normally used in a month.
mbrooke: In an electromechanical energy meter also when the load neutral is shared with other load neutrals, its reading may increase. But this is not shown in the image of your post 17.
If the meter is the old mechanical dial type, a high single month could well be the result of misreading the dials.
Sent from my XT1585 using Tapatalk
Absolutely. Before Rural POCO here got smart meters, users did need to submit meter reading each month when they make payment. Yes you could cheat if you wanted - they did from time to time read the meters themselves to correct anyone that was off. Some didn't exactly cheat so much as they just made their own estimate at times. All comes out in the end whenever it does get an accurate reading reported though. Well sort of anyway, there is different summer and winter rates for most customers here, as peak demand is during summer months and winter they have a lower rate somewhat just to encourage more energy usage during those months.If the meter is the old mechanical dial type, a high single month could well be the result of misreading the dials.
Sent from my XT1585 using Tapatalk
Absolutely. Before Rural POCO here got smart meters, users did need to submit meter reading each month when they make payment. Yes you could cheat if you wanted - they did from time to time read the meters themselves to correct anyone that was off. Some didn't exactly cheat so much as they just made their own estimate at times. All comes out in the end whenever it does get an accurate reading reported though. Well sort of anyway, there is different summer and winter rates for most customers here, as peak demand is during summer months and winter they have a lower rate somewhat just to encourage more energy usage during those months.
Had seen a few cases where someone wondered what was wrong when they got a higher then usual electric bill - come to find they misread meter or otherwise wrote wrong reading down.
mivey: Though TT system on our side and TN-S on POCO side, the individual ground rod resistance is very low, less than 1 ohm.
What is your soil resistivity? Rod length? A one ohm rod is pretty low. Not impossible but still...mivey: Though TT system on our side and TN-S on POCO side, the individual ground rod resistance is very low, less than 1 ohm.
Where and how did you measure that one ohm?mivey: Though TT system on our side and TN-S on POCO side, the individual ground rod resistance is very low, less than 1 ohm.
I live in an apartment.One evening, there was a problem with POCO neutral (disconection)and single phase supply to my apartment was off. It was high summer and no UPS in my apartment. My family members could not manage with candles. To alleviate the discomfort and to be sleep through the night, the neutral was connected to ground after the POCO meter and Lo and behold! The power supply to my apartment resumed and we slept peacefully. Next morning, the POCO neutral was set right. At the end of month I received POCO bill for electricity consumption for my apartment. I was shocked to find the bill amount was three times my usual bimonthly amount. I surmise that the return current that flowed over ground instead of through neutral during that neutral broken period might have encountered significant resistance, the power loss of which might have. increased the POCO meter reading. What are your views? Thanks.