Recalculate the load to avoid an upgrade of the service.
Charlypt
Florida
I have a client who wants to add some loads to a heavily loaded 200A, 240V, single-phase panel. It's an office building, 3200 sq ft.
They want to:
- add a washer and dryer (no idea why)
- a photocopier
- eliminate the break room.
Now, the engineer calculated that the panel exceeds the demand and proposes increasing the service to 400A. This would mean a very large expense for the client because it's practically a new service, a new panel, etc. They asked me what could be done to maintain the 200A service.
We proposed:
- first, eliminate the AC heaters; it's in Florida and they are practically unnecessary.
- Then, eliminate everything related to the break room: disposal unit, microwave, dishwasher, etc. Only the refrigerator remains. These loads are unused and can be eliminated.
The engineer provided some values for the lights and outlets, which I don't know where he got them from, but I followed them.
I proceeded to perform a new load calculation:
Lighting - using the given value of 1500 VA at 100%. Table 220.42
Receptacles: - given value 9800 VA at 100% (<10 kVA). Table 220.44
Washer 1200, Dryer 5800, Photocopier 1000, Fridge 1500: 100%
AC condensers (3 units): I used the MCA from the nameplate. Total 21400 VA at 100%. 440.6(A)
Air handlers (3 units): I used the value from the nameplate of the fans, because the heaters would be eliminated. 4600 VA at 100%.
With all this, I got 198 A. I don't understand how that panel could handle that load if the heaters added 40 kVA. Or am I calculating something wrong?
I have some questions about:
- Are AC units calculated at 100% or is only the largest one considered?
- Are AH units treated as motors, all of them or just the largest? If so, would they be calculated at 125%?
- Are the lights and outlets rated excessively and would require an on-site study or a recalculation based on the NEC?
- How could that panel have been approved with those heaters from the beginning?
- Are there any restrictions on using a service, disconnect, and panel at almost their maximum capacity?
Any help would be greatly appreciated. If possible, which NEC 2020 articles would justify this?
Thank you.
Use the largest of heating or cooling, not both.
MCA for the AC units already include a 125% value.
I used the MCA of each CU, but this way 125% is taken for each CU instead of the largest one. Should I take the MCA of the largest (125%) and the RLA of the other two? Then 100% of the AHUs, which are the remaining smaller motors.
I'm eliminating the heaters. I don't know how they could have been connected to that panel.
Can you do a 220.87 load calc instead? This uses a year's worth of 15 minute load data from the power company. Many power companies use smart meters now so they have this data, and I would think they have it for most commercial services since those tend to have demand charges.
NEC load calcs tend to be very conservative. My house comes to 145 amps calculated, but the highest 15 minute load data comes to about 55 amps. Even adding the required 125% to this gives me room for much more load.
Interesting. I never would have thought of that.
It means we can determine the true load by analyzing the usage log over a year. I was planning to just do a stress test one day, turn everything on and measure the load, but this is more realistic.
Thanks.
I have done "stress" tests too,,,, I agree, they coe out less than the calc and certainly less than the "speculation". For me its rare to see a 200 overloaded and one comes to mind was a tavern on hot summer and that calc list would even made a dent in it. Te reason the heaters didnt effect the load is they were rarely if any used.
A load calc is a guess,,, its a scientific guess. I rarely see overloads that were not on old 60 fuses,,, the houses had every major appliance added to them.. All electric. Had a bud with 1 and last straw was a new heavy microwave. Water heater, range, dryer, teenage family on old fuses. 200 is pretty resilient.
Some of those places had creative wiring to get it all hooked on.
Went thru this a bit ago. Neighbor calls and asks if I have a Zinsc or Murray maybe but I didnt and gave him masters number down the road has a small collection. The neighbor knows his way around a panel and said,,, I turned the place up and right around 50A. Couldnt find a 100,,, back fed a 50 and worked dandy. If they threw 3 kids at it maybe not.
I remember early on when I studied this, got all caught up in V drop and after I upgraded to 200 at the time couldnt figure how we ever did it from old 60 or 100 with long feeds to outbuildings where loads were lopsided and never calced, no balance, motors starting.
100% this right here. NEC load calcs are essentially meaningless and serve no purpose other that to satisfy authorities.
Yes, agree with this and very typical. The OP said in first post,,, heavily loaded which is not the same as a lot of connected equipment.
All that is overhead for me,,, meaning I figure they have their reasoning. But I still have the first amprobe I bought when I got interested in the ACTUAL load vs all the guessing and really cant recall cept for highly unusual biz that we se much heavy loading.
My inspector bud said it is becoming a thing though because of dope grows due to the fact resi being converted to them, a load calc does not apply to the help who simply plugs another lamp in till it smokes.
That's how I have always done load calcs - 125% or MCA for the largest unit, and RLA for the other units. However, someone else posted that the newer NEC's require MCA's to be used for all HVAC equipment.
Sure, they are normally very conservative (and they should be somewhat conservative). But without the load calcs, we are just guessing. You can't convince me that is better.
That's not quite right. It's MCA for the unit with the largest motor, and then for the other units, it's MCA - 25% of that unit's largest motor. Which if it's a simple unit with a compressor with RLA, a fan with FLA, and MCA = 125% * RLA + FLA, would be the same as RLA + FLA.
Reference?
Cheers, Wayne