Hi. Quick question.
On metal boxes self grounding receptacles are permitted and the receptacle wouldn't need a pigtail so that when it was removed from the box if would still be grounded ? Correct ?
Would 250.148B apply to removing the actually device would not interrupt grd continuity to the circuit but not the device or luminaire ? Correct ?
Thank you.
Hi. Quick question.
Correct assuming the box is grounded.
Thank you.
Correct. The removal of the above device will not affect the EGC continuity to downstream devices/lights.
So given the choice which would you use? I would go self-grounding every time. :)