Receptacle above baseboard heater?

Status
Not open for further replies.

SPierce

Member
Location
Nebraska
I thought there was a code that does not permit a receptacle to be located above a baseboard heater, but can't find it. All I see is an informational note and some commentary at the beginning of 210.52 saying that some baseboard heaters may come with instructions not permitting them to be installed below a receptacle. Is this all there is or is there a code regarding receptacle placement above a heater? Thanks for your help.
 
I thought there was a code that does not permit a receptacle to be located above a baseboard heater, but can't find it. All I see is an informational note and some commentary at the beginning of 210.52 saying that some baseboard heaters may come with instructions not permitting them to be installed below a receptacle. Is this all there is or is there a code regarding receptacle placement above a heater? Thanks for your help.

The information notes basically states that if the manufacturers instructions requires that no outlet be installed above the heater than you must follow it.

Informational Note: Listed baseboard heaters include instructions
that may not permit their installation below receptacle
outlets.

However these are allowed. They fit the corner spots on the heaters

images
 
There is more than art. 210 that has the informational note.

424.9 General. All fixed electric space-heating equipment shall be installed in an approved manner. Permanently installed electric baseboard heaters equipped with factory-installed receptacle outlets, or outlets provided as a separate listed assembly, shall be permitted in lieu of a receptacle outlet(s) that is required by 210.50(B). Such receptacle outlets shall not be connected to the heater circuits.


Informational Note: Listed baseboard heaters include instructions that may not permit their installation below receptacle outlets.
 