Receptacle behind fastened in place appliance

Subzero, Frigidaire, GE and others all make refrigerators and freezers which get fastened in place and cabinet doors attached to the front. They all - every one, without exception - have a dedicated space for receptacle behind the unit
 
  • Like
Reactions: kec
Yeah I guess that what it means. I never noticed that phrase before.

Ok so here is where we are at. A dishwasher has special requirements, so seems like a recep is not permitted in the dishwashers space per post #7.

But more generally, I am still not seeing s general requirement that a receptacle be accessible. Did I miss it? What about the case of the lamp in my walled in torture room?
Did not look it up, but whatever section that would prohibit burying a junction box in the wall should also apply to this. You have connections in the receptacle box, it needs to be accessible but doesn't have to be readily accessible unless in a specific situation that otherwise calls for it.
 
A little late to the party.

Has anyone since this thread looked at the 2023 NEC definition of "fastened-in-place?"

Fastened-n-place. Mounting means of equipment in which the fastening means are specifically designed to
permitted removal without the use of a tool.
 
This might help to explain.
Does this section apply to equipment supplied by the manufacturer? I know it’s a flexible cord, you know it’s a flexible cord, but does the code section apply since it came part of a listed assembly? A lot of times they don’t have any markings on them like a flexible cord I bought at the supply house would. Generally curious here, not arguing with you.
 