For new construction which is safer/better for new receptacle connections Loop/hook connection or back wire?
 
If the device is manufactured with pressure plate type connecting, ( as in spec grade and HG type receptacles) back wiring is the better choice IMO.

Roger
 
As stated above, when properly done, either will be as good as the other. In the old days, we back stabbed them all, no problems.[/QUOTE]

I sure hope you're not talking about the back stab ones I'm continually finding problems with!
 
As stated above, when properly done, either will be as good as the other. In the old days, we back stabbed them all, no problems.[/QUOTE]

I sure hope you're not talking about the back stab ones I'm continually finding problems with!

I'm guessing 99.9% of those failures were where the receptacle was used as a feed through device or had a heave load connected?

I have never done much service work but have run across more screw connection failures than back wiring failures. Most of the failures were receptacles used as feed through devices or had a heavy load (space heater) connected.

All of the projects I work on get back wired but always pigtailed. In the 31+ years I have been in business I have never had a call back from a failed connection.
 
As stated above, when properly done, either will be as good as the other. In the old days, we back stabbed them all, no problems.
If there were no problems why did UL change the rules to prohibit using the back stab connections with #12 wire?
 
If there were no problems why did UL change the rules to prohibit using the back stab connections with #12 wire?
Because if the receptacles are originally back-stabbed with #12 and then removed and re-used and back-stabbed with #14 this led to failures due to the contact points not grabbing the smaller wire tight enough.
 
By all means, please continue to use the backstab connections. :D

I love the margin on those service calls. Easy money.

Take apart a receptacle with both options available, and look at the surface area that you have available for conduction with the backstabs versus the screw terminals. No brainer. :dunce:
 
Last edited:
As stated above, when properly done, either will be as good as the other. In the old days, we back stabbed them all, no problems.

For clarification, in post number two I am not talking about back stab type devices. With that said, I agree that back stabbing is not always bad, I have devices that were back stabbed in a home that have been in place since the late 70's with no problems.

Roger
 
Because if the receptacles are originally back-stabbed with #12 and then removed and re-used and back-stabbed with #14 this led to failures due to the contact points not grabbing the smaller wire tight enough.

I seriously doubt that was the reasoning, However I was not active in the process at that time. My understanding is that for feed through the back stab cannot handle the load.

If the device is manufactured with pressure plate type connecting, ( as in spec grade and HG type receptacles) back wiring is the better choice IMO.

OOOOOh I hate those. I prefer a regular screw any day. Those clamp type garbage connectors come loose as you fold back the wires with 12 ga.

Roger

If there were no problems why did UL change the rules to prohibit using the back stab connections with #12 wire?

Because there werre plenty of failures. I have never seen a feed through fail when using the screws where they were installed correctly. However place a space heater on a backstab and you will have a failure. Just a mater of time.
 
quote_icon.png
Originally Posted by roger If the device is manufactured with pressure plate type connecting, ( as in spec grade and HG type receptacles) back wiring is the better choice IMO.

OOOOOh I hate those. I prefer a regular screw any day. Those clamp type garbage connectors come loose as you fold back the wires with 12 ga.

Roger

Where did you come up with that quote?

Roger
 
I seriously doubt that was the reasoning, However I was not active in the process at that time. My understanding is that for feed through the back stab cannot handle the load.





Because there werre plenty of failures. I have never seen a feed through fail when using the screws where they were installed correctly. However place a space heater on a backstab and you will have a failure. Just a mater of time.
Yes, where they were installed correctly. I too have seen more problems with screw connections than back stab.
 
Yes, where they were installed correctly. I too have seen more problems with screw connections than back stab.

So can you quantify those screw connections as failing overall, or due to poor original installation technique?

You just may be following a crew or even a whole company that just didn't care what happened after their check cleared.
 
So can you quantify those screw connections as failing overall, or due to poor original installation technique?

You just may be following a crew or even a whole company that just didn't care what happened after their check cleared.
Probably poor installation technique.

Maybe, or a whole bunch of companies that didn't care what happened after their check cleared.

No different than going over and finding a burnt wire at the breaker and giving the screw 3 or four good turns. How do you forget to tighten a screw?
 
Last edited:
Because if the receptacles are originally back-stabbed with #12 and then removed and re-used and back-stabbed with #14 this led to failures due to the contact points not grabbing the smaller wire tight enough.
Can you cite a source for that comment?
 
Yes, where they were installed correctly. I too have seen more problems with screw connections than back stab.
Personally I see more backstab than screw connection failures, however have run across groups of screw connection failures, seem to be related to torque setting on original installer's cordless. Or obviously sloppy loops.
 
I have noticed one thing about the backstabs over the years but i believe that it also affects screw terminals as well on a lesser scale...

heat damage is always obvious.

But i see way more that just pull out or work a terminal loose... and those have always been harder to explain.

When an outlet is installed, if the electrician does not fold all the wires in nicely behind it, it creates a lot of tension pushing the outlet back away from the box.

Then people push plugs into it and pull them out for 15 yrs and all that forward and backward motion is what i believe works those wires out.

The box is stationary, the outlet is stationary,(maybe) but with the wires on tension behind it, the wire works its way out tiny bits at a time til it pulls out.

Just my theory. No other way to explain how that much movement can happen in something that seems to not move...

Same theory with the screw terminals. The wire loops are round. The screw is round. Makes a nice hinge after 15 yrs of microscopic movement back and forth... stops making contact. Burns up... one little arc blast at a time...

My 2 cents worth...
 