NEC (2017) 348.60 - FMC, if flexibility is required after installation a ground conductor is required, but if not the FMC can act as the grounding conductor in accordance with 250.118(5), here it indicates a limited length of FMC otherwise a grounding conductor will be required.I think if you know the flex is there you should try to get a compliant EGC there, even if NEC isn't clear about what is required for existing situation.
GFCI may be an acceptable alternative. The problem with flex isn't that it won't carry ground fault current, but it could have enough impedance that overcurrent protection may be less effective and is the main reason for the six foot of flex being max allowed as an EGC path.
Had an odd thought, providing gfci protection for ungrounded receptacle when replacement with 3 prong, can a gfci breaker provide the same code compliance as a gfci receptacle, or does it need to be a receptacle type?