GerryB
Senior Member
- Location
- woodbridge, ct. USA
It is an elevator pit that requires a receptacle at the bottom of the pit, which is below the flood zone. Any way to do that?
There seems to be options available for a waterproof light and switch. For the outlet I would agree with winnie just an outdoor gfi and cover and replace if it goes bad. The elevator inspector wants it down there and our NEC doesn't get into flood zones so not much choice as I see it.Well you're required to have a switch and a light down there too and the lighting cannot be connected to the load side of a GFCI, so how were you planning on protecting them?
Well you're required to have a switch and a light down there too and the lighting cannot be connected to the load side of a GFCI, so how were you planning on protecting them?
No sump pump. Kinda funny because there is a drain in the floor that is to be closed since water can also come in that way.I would assume the light, and especially the switch for that, could be significantly higher than the required receptacle. But it's been a decade since I helped build an elevator and I was just doing what they told me, so have never studied those codes.
Is this for in case the sump pump doesn't work or is overwhelmed? Or is there no sump pump, and it's dewatered by other means after a flood?
Those pits usually aren't that deep so not that much higherI would assume the light, and especially the switch for that, could be significantly higher than the required receptacle. But it's been a decade since I helped build an elevator and I was just doing what they told me, so have never studied those codes.
Is this for in case the sump pump doesn't work or is overwhelmed? Or is there no sump pump, and it's dewatered by other means after a flood?
I'd go one step further and mount the GFCI up high in the dry zone, so you won't have a hot conductor submerged in floodwaters after the GFCI trips.... an ordinary GFCI receptacle installed in a non-corroding enclosure and non-corroding conduit would make the most sense, with the conduit routed out of the flood zone to an overhead junction box. That way, in the event of a flood, the thing could be quickly and cheaply replaced. ...