E Enrique Lara Member Location FL, USA Feb 15, 2019 #1 In commercial work should one be able to use the receptacle as a jumper instead of splicing ones wires and making a pigtail for ones neutral and hot? Is there any where in the code book I can reference this?
In commercial work should one be able to use the receptacle as a jumper instead of splicing ones wires and making a pigtail for ones neutral and hot? Is there any where in the code book I can reference this?
roger Moderator Staff member Location Fl Occupation Retired Electrician Feb 15, 2019 #2 Except for the neutrals of MWBC's you can use a device as a feed through for circuit conductors. See 300.13(B) Roger
Except for the neutrals of MWBC's you can use a device as a feed through for circuit conductors. See 300.13(B) Roger