At what distance can receptacles be installed in relation to the church baptistery.
I am not trying to be a smart-alec with this one:rroark0003 said:At what distance can receptacles be installed in relation to the church baptistery.
tallguy said:I'm a Baptist, and ours could arguably be considered a swimming pool for code purposes.
mdshunk said:After that, I immediately double checked to see that my church's baptistry heaters were on a GFCI breaker. They weren't, so I changed that.
mdshunk said:Agreed, and I'm a Baptist too. Treat it just like a pool with the same rules. This reminds me of the preacher a few years back that got killed in the baptistry when someone handed him the grounded microphone. I think the heating elements for the baptistry were shorted to the tank. After that, I immediately double checked to see that my church's baptistry heaters were on a GFCI breaker. They weren't, so I changed that.
tallguy said:To get back to the OP... Am I covering everything here??:
If it's a pool... 10' as per 680.22(A)(2) and must be GFCI within 20' as per 680.22(A)(5). Note 680.22(A)(6) though in regards to not taking this too literally -- i.e. you can have a recep. on the other side of a wall that is nevertheless within the radius.
If it's not a pool (nor a fountain, spa, etc.)... None of the circumstances listed in 210.8(B) apply, so... there must be something else that applies?:-? Otherwise, one could plop down a recep. right underneath it without GFCI. That doesn't pass the common sense test (then again, neither does a recep under a kitchen sink)...
No sweat. Just stick a little two circuit box at the panel and put in a conventional GFCI breaker. I don't think there's a blessed thing wrong with Pushmatics, save for the fact that they don't make them anymore.peter d said:Only problem is the panel is Pushmatic so some modification might be needed.
mdshunk said:I don't think there's a blessed thing wrong with Pushmatics, save for the fact that they don't make them anymore.
They do, and I might even have an NOS one. When Goulds was handling the Pushmatic name, they made some GFCI Pushmatics. Far easier to just come off a regular breaker and set a little two circuit QO or CH box, and put in a more normal GFCI breaker. Probably much cheaper. I think a 2-circuit box is only about 11 dollars.peter d said:I was more commenting on the fact that a Pushmatic GFCI breaker probably doesn't even exist. And if it does, it's likely to be obscenely expensive.
mdshunk said:Far easier to just come off a regular breaker and set a little two circuit QO or CH box, and put in a more normal GFCI breaker. Probably much cheaper. I think a 2-circuit box is only about 11 dollars.
Most do. If yours doesn't, I pity the people.peter d said:Once I investigate to see if the baptistry even has a heater, that's probably the solution that I'll use.![]()
Ours doesn't... haven't tried it for myself yet though!mdshunk said:Most do. If yours doesn't, I pity the people.Brrrrr.
I remember something happened to the thermostat in ours once, and when I went into the church, all the windows were fogged up and the whole building felt like a sauna. There were some pretty grumpy people that day. They ususally only turn it on several hours before a scheduled baptism, but for some reason it was on for several days that time.tallguy said:Ours doesn't... haven't tried it for myself yet though!
steve66 said:I remember that also. I think that was carried in newspapers across the country. However, I thought it was the microphone and audio equipment that was at fault. Seems like it wasn't grounded, or something like that.