Re: Receptacle rating for marina load calculation
On the marina study that I mentioned earlier, it was my recommendation that they bring 480 volt, 3-phase onto the pier. My design had three transformers on the pier, located at the one sixth, three sixths, and five sixths distance points along the pier. Each transformer was 480 ? 120/240, single phase, so I staggered the primary feeds (AB, then AC, then BC) to help equalize the primary currents. Each transformer fed slips both up and down the pier. In other words, the transformer at the one sixth point fed all slips along the first third of the pier. My design included use of power pedestals similar to the ones that hardworkingstiff described.
On the marina study that I mentioned earlier, it was my recommendation that they bring 480 volt, 3-phase onto the pier. My design had three transformers on the pier, located at the one sixth, three sixths, and five sixths distance points along the pier. Each transformer was 480 ? 120/240, single phase, so I staggered the primary feeds (AB, then AC, then BC) to help equalize the primary currents. Each transformer fed slips both up and down the pier. In other words, the transformer at the one sixth point fed all slips along the first third of the pier. My design included use of power pedestals similar to the ones that hardworkingstiff described.