Article talks about receptacle replacement. Changing out two prong receptacles and replacement them with grounded one. The use of GFCI in the place when there no ground.
 
Article talks about receptacle replacement. Changing out two prong receptacles and replacement them with grounded one. The use of GFCI in the place when there no ground.

replacing a nema-1 where no egc exists for a nema-5-gfi or nema-5 with gfi ocpd. sounds good. i don't like that rule, but whatever NEC says is it :thumbsup:. just be sure the little "no egc" sticker is on the faceplate.
 
I found what I was looking for. Article 406 ( D )(2) Non-Grounding-Type Receptacles ( c ). Thanks for the replies. Appreciate you looking. Couldn’t find it at first.
 
Just to add, if there is an EGC in any cabling between grounding receptacles used on a non-grounding circuit protected by a GFCI, you should not connect it to any receptacle terminal or box.

The reasoning is that a line-to-case/housing short within any plugged in appliance or equipment does not energize the case or housing of another appliance or equipment on the same circuit.
 
Just to add, if there is an EGC in any cabling between grounding receptacles used on a non-grounding circuit protected by a GFCI, you should not connect it to any receptacle terminal or box.

The reasoning is that a line-to-case/housing short within any plugged in appliance or equipment does not energize the case or housing of another appliance or equipment on the same circuit.


Good tip. :thumbsup:
 
Just to add, if there is an EGC in any cabling between grounding receptacles used on a non-grounding circuit protected by a GFCI, you should not connect it to any receptacle terminal or box.

The reasoning is that a line-to-case/housing short within any plugged in appliance or equipment does not energize the case or housing of another appliance or equipment on the same circuit.

Makes sense, but I thought you were not allowed to extend a non grounded circuit.
 