Receptacle replacements

Status
Not open for further replies.

fandi

Senior Member
Location
Los Angeles
Hello All,
This is for hotel guest rooms. For new installations, AFCI receptacles are required per 210.12(C). For receptacle replacement in general, section 406.4(D)(4) states that AFCI is required for receptacles in the areas specified in 210.12(A) or (B). But the code does not talk about 210.12(C) which is the reason I post this question: Is AFCI required for the replacement of existing receptacles in hotel guest rooms?
What is the code section that states that any modifications/changes of the existing conditions shall meet the current requirements of the current code?
Thank you.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That's a good question !
It seems inferred since 210.12(C) refers you back to 210.12(A) but you can sure make the argument that 406.4 doesn't require it,
 

fandi

Senior Member
Location
Los Angeles
That's a good question !
It seems inferred since 210.12(C) refers you back to 210.12(A) but you can sure make the argument that 406.4 doesn't require it,
Even 406.4 doesn't require it, 210.12(C) still requires it and doesn't modifying existing conditions mean the installers shall comply with the current code requirements? For example, a panel upgrade from 30A main shall have minimum 60A breaker per NEC 225.39(D)?
 

Meltric_South

Member
Location
Austin, TX
Occupation
Regional Sales Manager
Although not part of the requirements of NEC you might find what you are looking for in Informative Annex H - Administration and Enforcement.
 

kwired

Electron manager
Location
NE Nebraska
Even 406.4 doesn't require it, 210.12(C) still requires it and doesn't modifying existing conditions mean the installers shall comply with the current code requirements? For example, a panel upgrade from 30A main shall have minimum 60A breaker per NEC 225.39(D)?
Other code sections allow replacement of same thing in certain situations. Take an existing 3 wire range receptacle that maybe just worn out. You can generally replace it with another 3 wire presuming it didn't have something wrong from when it was installed. I think if anything this one probably intended to need to be updated to AFCI but maybe overlooked in code making process?
 

fandi

Senior Member
Location
Los Angeles
Other code sections allow replacement of same thing in certain situations. Take an existing 3 wire range receptacle that maybe just worn out. You can generally replace it with another 3 wire presuming it didn't have something wrong from when it was installed. I think if anything this one probably intended to need to be updated to AFCI but maybe overlooked in code making process?
Maybe.
 
D

Dell3c

Guest
Although not part of the requirements of NEC you might find what you are looking for in Informative Annex H - Administration and Enforcement.
As mentioned in the above from poster #5, in the 2017 Code Era.. Information Annex H,
Administration and Enforcement.
80.9 Applications
(A) New Installations
(B) Existing Installations
(C) Additions, Alterations or Repairs.

* I hope this helps..
 

fandi

Senior Member
Location
Los Angeles
As mentioned in the above from poster #5, in the 2017 Code Era.. Information Annex H,
Administration and Enforcement.
80.9 Applications
(A) New Installations
(B) Existing Installations
(C) Additions, Alterations or Repairs.

* I hope this helps..
Yes, I saw it after poster #5 mentioned Annex H. Thanks.
 