Receptacle Required In Bathroom

Status
Not open for further replies.
I have a question about required receptacles. Are receptacles required in bathrooms in restaurants? I know they are required in dwelling units, but can't find any definitive information about restaurants.

Thanks,

Jim
 
Re: Receptacle Required In Bathroom

If required does it have to be installed within 3' of the sink.I can't find it in the code either.I just inspected a storage building with a rest room in it.It did have a gfci receptacle installed but it was installed on the wall behind you as you stand in front of the sink.Probably about 6' away from the sink.This does not seem very safe at all.I decided not to red tag for it until I can find out for sure that it is a violation.
Paul
 
Re: Receptacle Required In Bathroom

If it's required, it would be a local code & you would need to talk to the ahj. Since the code does not require one, IMO, the recep. could be installed anywhere.
 
Re: Receptacle Required In Bathroom

Originally posted by bassphisher:This does not seem very safe at all.
I don't see anything unsafe about it. In a dwelling unit, you need a receptacle near the sink so that you can use the mirror while shaving or drying your hair (well, for me, just shaving). You don't usually do such things in a bathroom within a storage area or restaurant. So why is there a receptacle there at all? Who knows, and who cares? Perhaps it is for use by the cleaning crew who will be using a vacuum or buffer on the nearby floors.
Originally posted by bassphisher: I decided not to red tag for it until I can find out for sure that it is a violation.
Kudos to you for that decision.
 