Receptacle Spacing in Non Kitchen
Little Bill
Tennessee NEC:2017
Semi-Retired Electrician
If you have an area that is like a kitchen less the permanent cooking provisions, how are the counter receptacles to be spaced? I think they are calling this a "kitchenette".
Per NEC I'd say the six-twelve rule is all that is required.
For convenience of the user the kitchen counter rules are probably better choice to follow.
It will depend how the AHJ will interpret the "Kitchenette"
IMO, I would do the 24" & 48" requirement.
Does the NEC require any outlets in that location?
I would say it depends on where this "kitchenette" is located.
(C) Countertops.
In kitchens, pantries, breakfast rooms,
dining rooms, and similar areas of dwelling units, recep-
tacle outlets for countertop spaces shall be installed in ac-
cordance with 210.52(C)(1) through (C)(5)
(C) Countertops.
This is a "bonus" area above a garage that will be used as an apartment. It has a bedroom, bath, laundry, and the "kitchenette". There may be cabinets above the counter along with the lower cabinets below the counter. So basically everything except the stove.