- Tennessee NEC:2017
- Semi-Retired Electrician
If you have an area that is like a kitchen less the permanent cooking provisions, how are the counter receptacles to be spaced? I think they are calling this a "kitchenette".
I would say that this the key. What is there?
From the plans, just counter space on both sides of a sink.
Does the NEC require any outlets in that location?
I would say it depends on where this "kitchenette" is located.
(C) Countertops.
In kitchens, pantries, breakfast rooms,
dining rooms, and similar areas of dwelling units, recep-
tacle outlets for countertop spaces shall be installed in ac-
cordance with 210.52(C)(1) through (C)(5)