Receptacle spacing - other than residential

Status
Not open for further replies.

kiss

Senior Member
Is there any requirements for spacing of outlets in non residential installations? Also is the load calculation for these outlets at 180VA if actual load is not known? Thanks.
 
Re: Receptacle spacing - other than residential

I do not know of any specified locations in non dwelling units other than service outlets for HVAC roof top units. Aricle 220.3(B)(9) will give you the VA needed for your branch circuit calculations.
 