I do wish I had a job I could do that on because once you enter the real world where devices take up space and are not a theoretical point it would work I will give you that. Of course on most jobs Id probably be fired if I did it
Sent from my SM-G935P using Tapatalk
The Pythagorean theorem for outlet spacing. Lol. No, you measure along the floor line to get the length of the wall space, in this case 12 ft. Therefore 1 outlet in the center would meet the requirement of no part of the wall space being over 6 ft from a receptacle that is mounted lower than 5.5 ft. , not part of a lumnaire or appliance, not switch controlled, and not inside a cabinet (210.52).
Correct.If it is an inside corner, you could use a single floor receptacle placed in the corner, 18" off each wall.
If it's an outside corner, I don't think it is possible.
Cheers, Wayne
"Food for thought" question:
Residence has a 12 ft wall space between door openings and the only receptacle is a duplex mounted at 5' AFF which will power a flat screen.
Common sense dictates a more easily accessible receptacle is needed but what about a Code reference ?
210.52(A)(1) states "no point measured horizontally along the floor line in any wall space is more than 6 ft from a receptacle outlet". Does that cover this situation ? Does that measurement mean literally on the floor ?
If so, adding a duplex receptacle 18" AFF would not technically resolve the problem on a 12 ft wall as the 18" AF would make it slightly over 6' along the floor line![]()
I think it meets the wording of the code but is a **** design to have one receptacle behind a flatscreen serving a 12' wall. I'd probably one run receptacle at 18" AFF under the TV recep (provided no entertainment center was supposed to go there) and jump it from the TV recep... at least that's what I'd do if the inspector dinged the 1st install.
210.52(A)(2) does not mention the real world diagonal measurement from receptacle to floor point. If the recep is 18" AFF, then 6' away on the floor gives a hypotenuse of 6.18' or 6'2.2". A recep at 5.5' AFF gives a hypotenuse of 8.14' or 8' 1.68". Doesnt matter tho since both are over 6' cord lengths. Only way one outlet can serve a 12' wall w/o requiring a longer than 6' cord would be to mount it dead center horizontally in the baseboard (eta: or raise the plane of the object needing power to the same plane as the receptacle).
Exactly. The contractor balked at adding a receptacle as the one at 5 ft was centered on the wall. He asked for a Code reference. Since there is no "common sense Article" the inspector was looking for a reference to require the receptacle.
Agreed, so as a result the hypotenuse measurements are immaterial, code-wise, even though they would matter for a real power cord.210.52(A)(2) does not mention the real world diagonal measurement from receptacle to floor point.
I take the wording "measured horizontally along the floor line" to mean that all points (including the receptacle locations) should be projected onto the floor line before measuring the distance.
Cheers, Wayne
Now hold it.
Your explanation of the measurement makes too much sense.
The 1st 5 posts say specifically that's not the way you measure the distance, and now it is?
210.52(a)(2) does not mention that that's not the way it's supposed to be measured either, so is it a free for all and we're just going by what the accepted interpretation is?
JAP>
I take the phrase "measured along the floor line" to mean that your measuring tape (or other device) must be placed along the floor line. So the only way to measure to/from points not on the floor line itself is by projecting the point to the floor line.How do you take it to mean that ?
The notion of projecting a point to a straight line is well defined. For a point on a wall surface directly above the floor line, you just drop the point down vertically until you hit the floor line (assuming the floor line is level). Which is how the section is commonly understood.
Cheers, Wayne