Hello I am working on a project where we are installing a freezer for some medical equipment. The freezer draws 15Amps. The electrical engineer specs us to run #6 THHN from a 20A breaker 175' away. My question is can we tap the #6 at the receptale with #10's so it will work on a 20A duplex receptacle? I think that 210.19 (a) (4) Exception 1 will cover me. Also we have another 20A circuit feeding some Refriderators which is calling for #6 THHN. Can we tap in a ceiling junction box and run #10's as long as it is within 25 feet? All the equipment has the standard U ground cord caps.