So is everybody else in the world.I m confused after reading the NEC code, Can someone please explain it to me?
Thanks!
So is everybody else in the world.
Can you be more specific?
Electrical discussions only please. Counseling is available on other forums.I was confused even before I read the NEC.
Electrical discussions only please. Counseling is available on other forums.
You can't find the VA rating in the code book. It's not a code issue. The rating is a declaration by the manufacturer of what the device is capable of handling.What is the VA rating of simplex, duplex and quad receptacle according to NEC code? Where can I find the VA rating in the code book?
. But the simple answer is you assign 90 VA for each place into which you can insert a plug. A simplex is assigned 90 VA, a duplex is assigned 180 VA, and a quad is assigned 360 VA. Is that what you were asking?
I do not think so, Charlie.
220.14(I) Receptacle Outlets. Except as covered in 220.14(J)
and (K), receptacle outlets shall be calculated at not less
than 180 volt-amperes for each single or for each multiple
receptacle on one yoke.
Wow, I've been doing the same thing - counting 90VA for a simplex. Where the heck did I get that from? Did I just assume a simplex should be half a duplex? I wonder if the code was ever written that way.
Uh, anyone got a copy of "Charlie's Rule" handy? Oh, never mind. I found one. :dunce:I do not think so, Charlie.
Uh, anyone got a copy of "Charlie's Rule" handy? Oh, never mind. I found one. :dunce:
But the simple answer is you assign 90 VA for each place into which you can insert a plug. A simplex is assigned 90 VA, a duplex is assigned 180 VA, and a quad is assigned 360 VA. Is that what you were asking?
None of which applies to dwelling units .......