jumper Senior Member Location 3 Hr 2 Min from Winged Horses Nov 3, 2015 #21 rose1981 said: So, that means even a simplex is calculated as 180VA:blink:.....I always thought simplex is 90VA, duplex is 180VA and quad is 360VA Click to expand... Simplex is 180VA.
rose1981 said: So, that means even a simplex is calculated as 180VA:blink:.....I always thought simplex is 90VA, duplex is 180VA and quad is 360VA Click to expand... Simplex is 180VA.
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Nov 3, 2015 #22 The quad is 360 because it has two yokes, not because it has four receptacles. Four simplex in a four gang box would be 720.
The quad is 360 because it has two yokes, not because it has four receptacles. Four simplex in a four gang box would be 720.