S sparky377 New member Oct 13, 2005 #1 can 120volt outlets in 4square boxes with rs cover be mount directly on concrete floor facing the outlet in the up position??
can 120volt outlets in 4square boxes with rs cover be mount directly on concrete floor facing the outlet in the up position??
B bphgravity Senior Member Location Florida Oct 13, 2005 #2 Re: receptacles for equipment fastened in place Sure. Receptacles in countertops or similar work surfaces are the only locations this is prohibited. See secton 406.4(E)
Re: receptacles for equipment fastened in place Sure. Receptacles in countertops or similar work surfaces are the only locations this is prohibited. See secton 406.4(E)