Golfguy8
Member
- Location
- Charlotte, NC
- Occupation
- Electrical Engineer
Is it a code violation to hardwire multiple 20A receptacles from the output of a 2kVA, 120VAC UPS that has a 25A internal input breaker? The branch circuit feeding the UPS has a 30A breaker and #10 AWG wire. UPS manufacturer claims you can install a 30A upstream of the UPS as the UPS input breaker provides OCP for the loads. I understand the reasoning behind the 25A breaker to be sized for the full UPS load and the battery charging current, As well as the 30A panel breaker to protect the wires feeding the UPS.
However, My interpretation of the NEC is that you would need a 20A breaker at the panel and the 25A UPS breaker would not be allowed to be used as the OCP for the receptacles in order to meet the requirements in table 210.24(1). The receptacles will power multiple loads with a combined demand of 800W. Any feedback would be appreciated, I am an engineer who is relatively new to using the the NEC in my daily work.
However, My interpretation of the NEC is that you would need a 20A breaker at the panel and the 25A UPS breaker would not be allowed to be used as the OCP for the receptacles in order to meet the requirements in table 210.24(1). The receptacles will power multiple loads with a combined demand of 800W. Any feedback would be appreciated, I am an engineer who is relatively new to using the the NEC in my daily work.