Well, if your doing the entire house load, and running it to it's bare minimum, here's my thoughts. After your AFCI's for your bedrooms. After your 1500 VA's for SA for your kitchen, which can include also the dining , breakfast room and simliar areas. After your recept that's required for your laundry and last but not least your recept for your bath. 210.11 (B) states that the remaining portion needs to be evenly proportioned. So if you have 4 outlets left afterwards or 400, depending on your calculations needed for the amount of circuits, you can split 'em up evenly to hearts content.