Receptacles per circuit?

Status
Not open for further replies.
OK, I need an argument settled. I tell my yourneymen that when we design an electrical job I only want 10 recpts on a 15amp circuit and no more that 13 on a 20amp circuit. I maintain that this is code (quasi-code anyway since it seems to be in doubt) it is in the 2002 NEC-H 220.3(B)9 and exhibit 220.4. They say their other masters allowed them to put as many as 20 on a circuit. What's the general consensus?
 
15A=1800VA/180=10 - 20A=2400VA/180=13.3333333~
220.3(9) Receptacle Outlets. Except as covered in 220.3(B)(10), receptacle outlets shall be computed at not less than 180 volt-amperes for each single or for each multiple receptacle on one yoke. A single piece of equipment consisting of a multiple receptacle comprised of four or more receptacles shall be computed at not less than 90 volt-amperes per receptacle.
This provision shall not be applicable to the receptacle outlets specified in 210.11(C)(1) and (2).

Dwellings see 220.3(10) but agree, going too far with that leads to trouble.....
 
Joseph Alexander said:
OK, I need an argument settled. I tell my yourneymen that when we design an electrical job I only want 10 recpts on a 15amp circuit and no more that 13 on a 20amp circuit. I maintain that this is code (quasi-code anyway since it seems to be in doubt) it is in the 2002 NEC-H 220.3(B)9 and exhibit 220.4. They say their other masters allowed them to put as many as 20 on a circuit. What's the general consensus?

You must have worked with my boss, ( if talking residential ) its based on 3watts per sq ft. I laughed at my boss when he started counting outlets in a bedroom wondering if he should put the hall outlet on with them... :) o'well, I don't know everything either...
 
Last edited:
JohnJ0906 said:
It might be legal in residential, but bad practice.

John, why would it be a bad practice? It would certainly be better than a homeowner running 16 gauge extension cords everywhere to get to everything.

IMO, 99% of residential receptacle circuits (excluding SA's, bathrooms, and laundry) with 10 receptacles are probably not loaded to more than 2 or 3 amps at peaks times

Roger
 
roger said:
John, why would it be a bad practice? It would certainly be better than a homeowner running 16 gauge extension cords everywhere to get to everything.

IMO, 99% of residential receptacle circuits (excluding SA's, bathrooms, and laundry) with 10 receptacles are probably not loaded to more than 2 or 3 amps at peaks times

Roger
Your generous at 2-3 amps, all I have in my bedroom is a alarm clock.. :)
 
roger said:
John, why would it be a bad practice? It would certainly be better than a homeowner running 16 gauge extension cords everywhere to get to everything.

IMO, 99% of residential receptacle circuits (excluding SA's, bathrooms, and laundry) with 10 receptacles are probably not loaded to more than 2 or 3 amps at peaks times

Roger
remember, houses have spacing requirments to avoid exactly that. The number of recepticles per circuit does nothing to alter the total # of recepticles required. I guess I've too many cases of 2-3 bedrooms on one circuit, loaded a lot more than2-3 amps.
 
JohnJ0906 said:
remember, houses have spacing requirments to avoid exactly that..
And it doesn't always work, so why would we need extra circuits in a room just because we want to space them every 3 feet?

JohnJ0906 said:
The number of recepticles per circuit does nothing to alter the total # of recepticles required.
Absolutely, and if each receptacle that is required only has a connected load of .25 amps what are the odds of all 60 (15 amp circuit) being completely loaded at the same time?
 
These are the same circuits that window AC units get plugged into along with space heaters , dehumidifiers and vaccum cleaners alone that can pull 10 amps.

Guess I see this different than you guys , I think that whole idea of " because it's code and it says I can " is not always a good way of building things.
 
drg said:
These are the same circuits that window AC units get plugged into along with space heaters , dehumidifiers and vaccum cleaners alone that can pull 10 amps.

Guess I see this different than you guys , I think that whole idea of " because it's code and it says I can " is not always a good way of building things.

Absolutely.
 
drg said:
These are the same circuits that window AC units get plugged into along with space heaters , dehumidifiers and vaccum cleaners alone that can pull 10 amps.

Guess I see this different than you guys , I think that whole idea of " because it's code and it says I can " is not always a good way of building things.

nobody said we were wiring to code.... only telling what code is... thats what this forum is about CODE... CODE = MINIMUM requirements...
 
This forum is a little bit more involved than just code minimums...sometimes the discussions show its weak points and errors, and thats a good thing.

I don't always get led around by the nose by the NEC minimum requirements and think for myself on a rare occasion when I see the need to.
 
We used to have a point system of 2 points/ recep. and 1 point/ light outlet.#12 was 12 points and #14 was 10 points.Could you imagine what size panel would be required when 08 afci cycle comes into play,if that system(points) was still in effect ???? It`s hard enough keeping the AFCI breakers cool enough as it is.
 
roger said:
IMO, 99% of residential receptacle circuits (excluding SA's, bathrooms, and laundry) with 10 receptacles are probably not loaded to more than 2 or 3 amps at peaks times

Roger

Depends on the house.... Some people are minimalist, some - like the one I am doing now have a the makings of a home office and AV showroom in every room. The fact that everything outside of 210.11(C) could be on one circuit would not cut it for them.

I try to at the very least try to think about the use of areas.
 
stickboy1375 said:
If only my alarm clock had a grounded cord I wouldent need arc fault protection...

How do you figure that ?And what about lights? I agree many use very little but right now on master bedroom circuit 2 computers ,1 tv, dvr box ,few lights are on.Still far under 1800 watts.
 
e57 said:
Depends on the house....

Mark, that's why I said 99%

e57 said:
I try to at the very least try to think about the use of areas.

And knowing what the area (or circuit) is going (or may) to be used for would definitely change it from being just a general receptacle circuit, now we would address it with this knowledge in hand.

Roger
 
drg said:
This forum is a little bit more involved than just code minimums...sometimes the discussions show its weak points and errors, and thats a good thing.

Where is the 'General Discussions' section?

What I mean is this forum IMO is set up more for code talk than discussing which method is better or worse.


I don't always get led around by the nose by the NEC minimum requirements and think for myself on a rare occasion when I see the need to.

Many of us do that, however when I have to think for myself I like to have as much knowledge about the subject as I can get.

Knowing the code rules is just one part of the decision making process.
 