There have been past threads that discuss the use of 15A rated receptacles on 20A SA circuits. Am I correct that the reason this is allowed is because the 15A receptacle is built to 20A specifications and not because the 15A receptacle will reject a 20A plug? This makes sense because if a device drawing 18A was rewired with a 15A rated plug and plugged into a 20A circuit, the receptacle would not withstand the current if it were not built to handle 20A.
Assuming the above statement is true then it would be a violation to use a 20A rated receptacle on a 30A circuit regardless of the fact that it could not accept a 30A plug because the 20A receptacle is not built to 30A specifications, correct?
What guarantees that a receptacle manufacturer builds their 15A receptacles to 20A rated specifications?
Bob
Assuming the above statement is true then it would be a violation to use a 20A rated receptacle on a 30A circuit regardless of the fact that it could not accept a 30A plug because the 20A receptacle is not built to 30A specifications, correct?
What guarantees that a receptacle manufacturer builds their 15A receptacles to 20A rated specifications?