Re: Receptacles
We have to remember that 210.21(B)(1) is not just addressing 15 and 20 amp 120 volt receptacles but receptacles of any size.
For instance many people will supply a range with a 40 amp circuit equipped with a 50 amp receptacle. There are no forty amp receptacles that I am aware of.
Another example is in larger work, imagine I have a cord and plug connected piece of equipment rated 125 amps. I would most likely have to use a 200 amp rated receptacle for that, however I could feed that 200 amp receptacle with a 125 amp circuit sized for the machine.
All that said has anyone seen something that suggests the code as written is not working?
[ November 03, 2005, 05:25 AM: Message edited by: iwire ]
I would say one reason for using only a single receptacle is in fact just to take advantage of using a smaller OCP.Originally posted by goldstar:
This has always confused me. What are the reasons for using a single receptacle? Because you don't want any other appliances plugged into that location? Or that circuit?A single 20 amp receptacle is permitted on a 15 amp circuit. See 210.21(B)(1). A single 15 amp receptacle on a 20 amp circuit is not.
We have to remember that 210.21(B)(1) is not just addressing 15 and 20 amp 120 volt receptacles but receptacles of any size.
For instance many people will supply a range with a 40 amp circuit equipped with a 50 amp receptacle. There are no forty amp receptacles that I am aware of.
Another example is in larger work, imagine I have a cord and plug connected piece of equipment rated 125 amps. I would most likely have to use a 200 amp rated receptacle for that, however I could feed that 200 amp receptacle with a 125 amp circuit sized for the machine.
All that said has anyone seen something that suggests the code as written is not working?