Can you install a 120v outlet above a T-bar ceiling for a piece of equipment in the ceiling that plugs in? The cord does not penetrate the ceiling everything is above the T-bar.
Can you install a 120v outlet above a T-bar ceiling for a piece of equipment in the ceiling that plugs in? The cord does not penetrate the ceiling everything is above the T-bar.
is there a code referance for this
What would be the reason for ever installing a receptacle above a t-bar if you cant plug anything into it anyway,. For maintenance work maybe?
400.8 also0 refers you back to 400.7. Seems this could be subject to interpretation, would it not?
The example that comes to mind would be a UL listed cord connected condesate pump for an HVAC unit in the ceiling, that seems to fall under 400.7(8). :-?
\The example that comes to mind would be a UL listed cord connected condesate pump for an HVAC unit in the ceiling, that seems to fall under 400.7(8). :-?
The point I am getting at is, if it is an absolute rule, then how come 400.8 allows us to reffer to 400.7?
400.8 says "unless specifically permitted in 400.7".
I am not starting a war here just trying to be constructive.
There is nothing in 400.7 that specifically permits cords above ceilings.
Hanging strip lights in a grocery store.
Not to me, in my opinion the NEC clearly prohibits all cords covered by Article 400 from being installed above ceilings.
![]()