T tesi1 Member Location florida Jun 21, 2011 #1 on a 50 amp 125/250 volt 4-wire range / and or power outlet, are they listed for use with 60 or 75 degree conductors:huh:
on a 50 amp 125/250 volt 4-wire range / and or power outlet, are they listed for use with 60 or 75 degree conductors:huh:
R roger3829 Senior Member Location Torrington, CT Jun 21, 2011 #2 Yes. You need to check the label on the box, instructions, or the receptacle itself should have markings on it.
Yes. You need to check the label on the box, instructions, or the receptacle itself should have markings on it.