....in the main panel...is this legit? Does wrapping with white tape "cure" it if it is a problem?
....in the main panel...is this legit? Does wrapping with white tape "cure" it if it is a problem?
I assume you mean with the neutral bar. For wire sizes 6 gauge and smaller, they cannot be reidentified white, 200.6. if they are above 6 gauge, they can be reidentified with tape, see 200.6 (B).
Red wires running to a neutral bar is a violation.
There's an exception under 200.6(E) that allows white tape to be applied on multiconductors.
Yes, there are two exceptions under 200.6 (E). Neither of them permit you to remark an existing conductor even is in a multi conductor cable.
An inspector may not have an issue with somebody putting white tape or paint or whatever on an existing black or red cable to make it a neutral, however in my opinion it is a code violation in that section as written
We do it all the time for new construction in petro-chem facilities. Not sure about an existing conductor, but then again, this was not mentioned by the OP.
We do it all the time for new construction in petro-chem facilities. Not sure about an existing conductor, but then again, this was not mentioned by the OP.
residential
In new construction it is fine. The language that trips it up is "at the time of installation". What you are doing is fine, remarking existing conductors as neutrals is not.
Though Tony did not expressly imply the wiring is existing, I took his question to mean that they were and that he was looking at a panel with red wires going to the neutral bar.
Next question is what other conductors are in the cable? If there is already a white then that should be used for grounded conductor. There are some cables out there with no white conductor - I think you can re-identify any conductor in them other than a green, which must be used for EGC, with white if you are needing a grounded conductor in that situation.There's an exception under 200.6(E) that allows white tape to be applied on multiconductors.
My thoughts as well. If you aren't messing with the branch circuit but just replacing the panel some things go back the way they started out.I’m there to upgrade a service entrance. I see a red wire on the neutral bar and determine that it has been used as an EG since the day it was installed thirty years ago. Do I ID it as an EQ at both ends by stripping it out, wrapping a piece of green tape on it, or spend three days fishing a new compliant cable to the third floor? Let me think about this a minute.